You can configure the router’s General Purpose Input/Output (GPIO) pins in AirLink OS. The pins can be used to turn switches on and off, or report data such as temperatures, pressures and flow rates.
The XR router has five I/O pins available for input/output configuration:
| HARDWARE PIN NUMBER | LOCATION | AIRLINK OS ID | CONFIGURABLE FUNCTIONS |
|---|---|---|---|
| 4 | Power Connector | Primary IO | Digital Input and Output, Analog Input 1 |
| 7 | Auxiliary I/O | GPIO 2 | Digital Input, Analog Input |
| 6 | Auxiliary I/O | GPIO 3 | Digital Input, Analog Input |
| 3 | Auxiliary I/O | GPIO 4 | Digital Input |
| 2 | Auxiliary I/O | GPIO 5 | Digital Input |
1. The power connector GPIO (pin 4) digital input can also be used to put the device into a standby mode and to wake the router up.
For more information, refer to the Hardware Guide for the XR router.
To set the mode for each pin:
Go to System > I/O > Configuration
Select the Mode. The mode settings available are:
Once the Mode is selected, a corresponding entry will appear in the Analog Inputs table or the Digital Inputs and Digital Outputs tables.
Analog inputs monitor a voltage range in small increments. This allows you to monitor equipment that reports status as an analog voltage. Examples include:
In the Analog Inputs Table you can transform the voltage readings to a more convenient unit of measurement. For example, degrees Celsius or Fahrenheit for temperature, liters for volume, etc.
Before you configure, you need to locate or calculate the coefficient and the offset values.
Consult the user documentation for the equipment you want to monitor. It should provide you with the coefficient to convert volts to the appropriate unit of measurement and the offset value (the difference between the equivalent value for 0 volts and 0), or provide information on equivalent values for voltage readings from which you can calculate the coefficient and offset. (If this information is not available in the user documentation, contact the manufacturer.)
For example, if the equipment monitors temperature, and has a scale from 0 volts to 30 volts, the equipment specifications should provide information similar to the following:
0 V is equivalent to –20°C
30 V is equivalent to 100°C
This is expressed algebraically as follows:
a * 0V + b = –20C
a * 30V + b = 100C
where:
a = coefficient
b = offset
For this example, you can calculate a as follows:
(a * 30V + b) – (a * 0V + b) = 100C – (–20)
a * 30V = 120V
a = 4
To calculate b, substitute a into the first equation above:
4 * 0V + b = –20
b = –20
For each of the analog inputs you want to configure:
Go to System > I/O > Analog Inputs.
Enter the values for the coefficient and offset. (In this example, the coefficient is 4 and the offset is –20.)
AirLink OS will show the value of the transformed analog input.
Digital inputs monitor contact closures on a switch. This allows you to monitor changes such as:
When the trunk of a vehicle is opened or closed
The Digital Inputs Table displays:
For each of the digital inputs you want to configure:
Go to System > I/O > Digital Inputs.
In the DIGITAL INPUTS TABLE, select Active High or Active Low.
Enable/disable the Pull Up.
The power connector GPIO (pin 4) digital input can also be used to put the device into a standby mode and to wake the router up. To configure this, see Configuring Power Settings (MCU) .
When Power Connector pin 4 is configured as Digital Input and Output, you can configure the Digital Outputs settings. You can use Digital Output to drive a relay or for other uses where a switchable low-side current sink is required.
To enable Digital Output:
Go to System > I/O > Digital Outputs.
In the DIGITAL OUTPUTS TABLE, set Digital Outputs to Pin Grounded.
To view the status of the router’s GPIOs, go to Status > System > I/O (or click the link under Configuration).
The I/O STATUS table shows each enabled I/O Pin and its:
The transformation function uses Raw Value in units of volts, not millivolts, to display the Transformed Value.
Data sampling is taken over 20 measurements during a 250 ms interval. The measurements are averaged to generate a sample. If the sample has changed by the amount of the Deadband or a time period of 2.5 minutes has passed, then the Raw Value is updated.
If you want to add GPIO state to reports, you can do so in a custom report. See Services > Telemetry > Custom Reports.